Point: 0/404 Alarm: 0/136 Trip: 0/51 Point 0.0% Alarm 0.0 Trip0.0%
588CWCO | g588CWVCMDO COOLING WATER VALVE COMMAND | dwg.5NP209/2 | _51PM101.1.5.1.7 | D |
---|
[101] Gen.Differential Prot. |
[102] Generator Overvoltage |
[103] Gen.Neg.Phase Sequence |
[104] Gen.Minimum Impedance |
[105] Gen.Stator Earth Fault |
[106] Gen.Rotor Earth Fault |
[107] Generator Breaker FAIL |
[108] Excitation Field FAILURE |
[109] Excitation FAULT |
[110] Excite Transf. Overcurrent |
[111] 86-1 Relay Operated |
[112] 86-2 Relay Operated |
[113] 86-3 Relay Operated |
[114] Prot.DRS System Failure Stage 2 |
[115] Gen.Guide Bear.Temp.HIGH |
[116] Gen.Thr.Bear.Temp. HIGH |
[117] Gen.Winding Temp.HIGH Ph.A/B/C |
[118] Rotor Winding Temp.HIGH |
[119] Emergency Shutdown Valve |
[120] Quick Shutdown PB Operate |
[121] Tu.El.Overspeed Operated |
[122] Turbine Mech.Overspeed |
[123] Gen.CB Air Pressure LOW |
[124] Gen.CB Ins.Gas Press.LOW |
[125] Gov.Oil Pressure LOW |
[126] Unit CO2 Operated |
[127] Turb.Guid.Bear.Temp.HIGH |
[128] Oil Press.Tank oil Level LOW |
[129] Gen.or Turb. Vibration HIGH |
[130] Gov.Supply 1 and 2 FAIL |
[131] Gen.Bearing Oil Resv.Level LOW |
[132] Intake Gate Closing |
[133] KG3A Ph.C Press.Relief |
[134] KG3A Ph.C Buchholz Relay |
[135] KG3A Winding Temp.Phase C |
[136] KG3A Ph.C Tap Changer |
[137] KG3A Lockout Relay 86-TR |
[138] KG3A Transf.Diff.Protection |
[139] KG3A Overcurrent |
[140] Generator Undervoltage |
[141] Gen.Rotor Earth Fault |
[142] Excitation FAULT |
[143] Protection Test |
[144] Relay Volt.Unbalanced Operated |
[145] Rotor Earth Fault Prot.Relay Failure |
[146] Unit Contr.Board MCB TRIP |
[147] Unit MCC 52A TRIP |
[148] MCC Fault OR Air Cool.Sys.Fan FAULT |
[149] G.Bear.Oil Standby P. ON |
[150] HP Oil Pump Press. LOW |
[151] Gen.Guide Bear.Temp.HIGH |
[152] Gen.Thr.Bear.Temp. HIGH |
[153] Gen.Bear.Oil Temp. HIGH |
[154] Gen.Bear.Oil Lev.HI/LOW |
[155] Gen.Bearing Oil Flow LOW |
[156] Gen.Winding Temp.HIGH Ph.A/B/C |
[157] Gen.Air Cool.CW Flow LOW |
[158] Gen.Bear.Oil CW Flow LOW |
[159] Gen.or Turb.Vibrat. HIGH |
[160] Pneu.Brake Air Press.LOW |
[161] Tu.Bear.Oil Standby P.ON |
[162] Gov.Oil Filter 1or 2 Contaminated |
[163] Gov.Oil Standby Pump ON |
[164] Turb.Guid.Bear.Temp.HIGH |
[165] Turb.GB Oil Temp. HIGH |
[166] Turb.GB Oil Lev.HIGH/LOW |
[167] Turb.GB.CW Flow LOW |
[168] Turb.GB Oil Flow LOW |
[169] GV Shear Pin Broken |
[170] Gen.CB Ctrl.Volt. Loss |
[171] Gen.DS. Pole Disagreement |
[172] Gen.CB Ins.Gas Press.LOW |
[173] Unit Uncompl.Start/Stop |
[174] Intake Gate Lower |
[175] Unit CO2 Undervoltage |
[176] Power Ctrl.Deviat. High |
[177] Oil Press.Tank oil Level LOW/HI |
[178] Gov.Oil Reservoir Level too LOW |
[179] Gov.Cont.MCB TRIP or 24 VDC FAIL |
[180] Unit Creep Detect.Operate |
[181] Unit Seq. Controller FAULT |
[182] Turb.Shaft Seal CW Press.LOW |
[183] Unit CO2 Locked |
[184] KG3A Ph.C Cooling Oil |
[185] KG3A Ph.C Cooling Oil |
[186] KG3A Winding Temp.Phase A.B.C |
[187] KG3A Cooling Oil Pump Fault |
[188] KG3A Ph.A.B.C Oil Temp.HIGH |
[189] KG3A Ph.C Buchholz Relay |
[190] KG3A Ph.C CW TROUBLE |
[191] KG3A Ph.A.B.C Oil Level LOW |
[192] KG3A Ph.A.B.C Oil Level LOW |
[193] KG3A Ph.A.B.C Oil Level LOW |
[194] KG3A Ph.A.B.C Oil Level LOW |
[195] KG3A Ph.A.B.C Oil Level LOW |
[196] KG3A Ph.A.B.C Oil Level LOW |