Point: 0/ Alarm: 0/0 Trip: 0/0 Point 0.0% Alarm 0.0 Trip0.0%
|
[101] Gen.Differential Prot. |
[102] Generator Overvoltage |
[103] Gen.Neg.Phase Sequence |
[104] Gen.Minimum Impedance |
[105] Gen.Stator Earth Fault |
[106] Gen.Rotor Earth Fault |
[107] Dyn.Brake > I/Gen.Brk.Fail |
[108] Excitation Field FAILURE |
[109] Excitation FAULT |
[110] Excite Transf. Overcurrent |
[111] 86-1 Relay Operated |
[112] 86-2 Relay Operated |
|
[113] 86-3 Relay Operated |
[114] Prot.DC/DC 1 and 2 FAULT |
[115] Gen.Guide Bear.Temp.HIGH |
[116] Gen.Thr.Bear.Temp. HIGH |
[117] Gen.Winding Temp.Ph.A/B/C |
[118] Rotor Winding Temp.HIGH |
[119] Emergency Shutdown Valve |
[120] GA_Emergency Stop PB |
[121] Tu.El.Overspeed Operated |
[122] Turbine Mech.Overspeed |
[123] Gen.CB Air Pressure LOW |
[124] Gen.CB Ins.Gas Press.LOW |
|
[125] Gov.Oil Pressure LOW |
[126] Unit CO2 Operated |
[127] Turb.Guid.Bear.Temp.HIGH |
[128] Tur.Brg.Oil Res.Level LOW-LOW |
[129] Gen.or Turb.Vibrat. HIGH |
[130] Gov.Supply 1 and 2 FAIL |
[131] Gen.B.Oil Reservior Level LOW |
[132] Intake Gate Closing |
[133] |
[134] |
[135] |
[136] |
|
[137] |
[138] |
[139] |
[140] Generator Undervoltage |
[141] Gen.Rotor Earth Fault |
[142] Exc.AVR Mode MANUAL |
[143] Protection Test |
[144] Volt.Unbalanced Operated |