ANNUNCIATOR (15F) U2

  CHECKED :                  
H56    edit ID334 IX1.8.4.7 Input 7 Gen.Winding Temp.Ph.A/B/C ALARM 2GD008/SH46
 
  TARGET :           

[1]
Generator Differential TRIPPED
[2]
Generator Overvoltage TRIPPED
[3]
Gen.Negative Phase Sequence TRIPPED
[4]
Gen.Minimum Impedance TRIPPED
[5]
Gen.Stator Earth FAULT TRIPPED
[6]
Rotor Earth Fault TRIPPED
[7]
Dyn.Brake Overcurrent/Gen.Brk.FAIL TRIPPED
[8]
Excit.Field FAILURE TRIPPED
[9]
Excitation FAULT TRIPPED
[10]
Excit.Transformer Overcurrent TRIPPED
[11]
86-1 Relay Operated TRIPPED
[12]
86-2 Relay Operated TRIPPED
[13]
86-3 Relay Operated TRIPPED
[14]
Protection DC/DC. 1 and 2 FAULT TRIPPED
[15]
Gen.Guide Bearing Temp.HIGH TRIPPED
[16]
Gen.Thrust Bearing Temp.HIGH TRIPPED
[17]
Gen.Winding Temp.Ph.A/B/C TRIPPED
[18]
Rotor Winding Temp.HIGH TRIPPED
[19]
Emergency Shutdown Valve TRIPPED
[20]
Quick Shutdown PB.Operate TRIPPED
[21]
Electrical Overspeed Operated TRIPPED
[22]
Turbine Mechanical OVER SPEED TRIPPED
[23]
Gen.CB. Air Pressure LOW TRIPPED
[24]
GCB.Ins.Gas Pressure LOW 2nd TRIPPED
[25]
Gov.Oil Pressure LOW TRIPPED
[26]
Unit CO2 Operated TRIPPED
[27]
Turb.Guide Bearing Temp.HIGH TRIPPED
[28]
Gov.Oil Pressure Tank oil level LOW TRIPPED
[29]
Gen.or Turb.Shaft Vibration HIGH TRIPPED
[30]
Electronic Gov.TROUBLE TRIPPED
[31]
Gov.Oil Reserv. Tank Oil Level LOW TRIPPED
[32]
Intake Gate Closing TRIPPED
[33]
STATION SERVICE TR Over current
[34]
KG1A/C Fire Fight.Sys.Water Sprayed TRIPPED
[35]
Inverter FAULT ALARM
[36]
Inverter Voltage TROUBLE ALARM
[37]
Synchronizer Trouble ALARM
[38]
SER Trouble
[39]
Electronic Console DC. FAIL ALARM
[40]
Generator Undervoltage ALARM
[41]
Rotor Earth Fault ALARM
[42]
Excitation FAULT ALARM
[43]
Protection Test ALARM
[44]
Relay Voltage Unbalance Operate ALARM
[45]
Protection DC/DC 1 or 2 FAULT ALARM
[46]
Unit 2 Control Board MCB TRIP ALARM
[47]
Unit 2 Control Board MCB TRIP ALARM
[48]
Unit 2 MCC.Under Voltage ALARM
[49]
Gen.Bear.Oil Standby Pump Run ALARM
[50]
HP. Oil Pump Pressure LOW ALARM
[51]
Gen.Guide Bearing Temp.HIGH ALARM
[52]
Gen.Thrust Bearing Temp.HIGH ALARM
[53]
Gen.Bearing Oil Temp.HIGH ALARM
[54]
Gen.Bearing Oil Level LOW/HIGH ALARM
[55]
Gen.Bearing Oil Flow LOW ALARM
[56]
Gen.Winding Temp.Ph.A/B/C ALARM
[57]
Gen.Air Cooler CW.Flow LOW ALARM
[58]
Gen.Bearing Oil CW.Flow LOW ALARM
[59]
Gen.or Turb. Vibration HIGH ALARM
[60]
Pneumatic Brake Air Pressure LOW ALARM
[61]
Tur.Bear.Oil Circ.Standby Pump Run ALARM
[62]
Gov.Oil Pressure LOW ALARM
[63]
Gov.Oil Standby Pump RUN ALARM
[64]
Turb.Guide Bearing Temp.HIGH ALARM
[65]
Turb. GB. Oil Temp. HIGH ALARM
[66]
Turb.GB.Oil Level LOW/HIGH ALARM
[67]
Turb.GB.CW.Flow LOW ALARM
[68]
Turb.GB.Oil Flow LOW ALARM
[69]
Shear pin Broken ALARM
[70]
Gen.CB.FAULT ALARM
[71]
Dyn.Brake/Gen. DS.FAULT ALARM
[72]
GCB.Ins.Gas Pressure LOW 1st ALARM
[73]
Uncomplete Start/Stop ALARM
[74]
Intake Gate Under Voltage ALARM
[75]
E!B TIE BREAKER CLOSE
[76]
Control Deviation HIGH ALARM
[77]
Oil Pressure Tank Level LOW ALARM
[78]
Gov.Oil Tank Oil Reserv.Level HI/LO ALARM
[79]
Gov.Oil Tank Oil Reserv.Level HI/LO ALARM
[80]
Unit Creep Detector Operate ALARM
[81]
Unit Sequence Controller TROUBLE ALARM
[82]
Turb.Shaft Seal CW.Press.LOW ALARM
[83]
CO2 Locked ALARM
[84]
Chager 1 TROUBLE ALARM
[85]
GROUP LAMP
[86]
Chager 2 TROUBLE ALARM
[87]
DC.Circuit Volt TROUBLE ALARM
[88]
DC.Circuit Ground FAULT ALARM
[89]
DC Distribution Feeder TRIP ALARM
[90]
Charger 1 or 2 AC.Supply FAIL ALARM
[91]
KG1A Fire Fighting System FAIL ALARM
[92]
-
[93]
Turbine Manual
[94]
Line Charging TEST
[95]
-
[96]
PILOT LAMP