ANNUNCIATOR (13F) U1

  CHECKED :                  
H68    edit IX1.6.8.7 Input 7 Turb.GB.Oil Flow LOW ALARM GD008/SH29 GD002/SH4
 
  TARGET :           

[1]
Generator Differential TRIPPED
[2]
Generator Overvoltage TRIPPED
[3]
Gen.Negative Phase Sequence TRIPPED
[4]
Gen.Minimum Impedance TRIPPED
[5]
Gen.Stator Earth FAULT TRIPPED
[6]
Rotor Earth Fault TRIPPED
[7]
Dynamic Brake Overcurrent/Gen Brk.FAIL TRIPPED
[8]
Excitation Field FAILURE TRIPPED
[9]
Excitation FAULT TRIPPED
[10]
Excit.Transformer Overcurrent TRIPPED
[11]
86-1 Relay Operated TRIPPED
[12]
86-2 Relay Operated TRIPPED
[13]
86-3 Relay Operated TRIPPED
[14]
Protection DC/DC.1 and 2 FAULT TRIPPED
[15]
Gen.Guide Bearing Temp.HIGH TRIPPED
[16]
Gen.Thrust Bearing Temp.HIGH TRIPPED
[17]
Gen.Windg.Temp.Ph.A/B/C TRIPPED
[18]
Rotor Winding Temp.HIGH TRIPPED
[19]
Emergency Shutdown Valve TRIPPED
[20]
Control Board Emergency Stop ON
[21]
Electrical Overspeed Operated TRIPPED
[22]
Turbine Mechanical OVER SPEED TRIPPED
[23]
Gen.CB. Air Pressure LOW TRIPPED
[24]
GCB.Ins.Gas Pressure LOW 2nd TRIPPED
[25]
Governor Oil Pressure LOW TRIPPED
[26]
Unit CO2 Operated TRIPPED
[27]
Turb.Guide Bearing Temp.HIGH TRIPPED
[28]
Gov.Oil Pressure Tank Oil Level LOW TRIPPED
[29]
Gen.or.Turb.Shaft Vibration HIGH TRIPPED
[30]
Electronic Governor TROUBLE TRIPPED
[31]
Governor Oil Reserv.tank Oil Level LOW TRIPPED
[32]
Intake Gate CLOSED
[33]
KG1A/C Press.Relief Dev.Operated TRIPPED
[34]
KG1A/C Buchholz Relay TRIPPED
[35]
KG1A / B Winding Temp. TRIPPED
[36]
KG1A/C Tap Change Mis/Oil Level LOLO TRIPPED
[37]
KG1A Lockout Relay 86-TR TRIPPED
[38]
Main Transformer Differential TRIPPED
[39]
Main Transformer Overcurrent TRIPPED
[40]
Generator Undervoltage ALARM
[41]
Rotor Earth Fault ALARM
[42]
Excitation FAULT ALARM
[43]
Protection Test ALARM
[44]
Rel.Volt.Unbalance Operated ALARM
[45]
Protection AC. Supply FAULT ALARM
[46]
Unit1 Control Board MCB.TRIP ALARM
[47]
MCC. E1A. CB.TRIP ALARM
[48]
MCC Fault /Air Admission Valve FAULT ALARM/..
[49]
Gen.Bearing Oil Standby Pump Run ALARM
[50]
HP. Oil Pump Pressure LOW ALARM
[51]
Gen.Guide Bearing Temp.HIGH ALARM
[52]
Gen.Thrust Bearing Temp.HIGH ALARM
[53]
Gen.Bearing Oil Temp.HIGH ALARM
[54]
Gen.Bearing Oil Level LOW or HIGH ALARM
[55]
Gen.Bearing Oil Level LOW or HIGH ALARM
[56]
Gen.Windg.Temp.Ph.A/B/C ALARM
[57]
Gen.Air Cooler CW.Flow LOW ALARM
[58]
Gen.Bearing Oil CW.Flow LOW ALARM
[59]
Gen.or Turb. Vibrat.HIGH ALARM
[60]
Pneumatic Brake Air Pressure LOW ALARM
[61]
Turb.Bear.Oil circ.Standby Pump Run ALARM
[62]
Governor Oil Pressure LOW ALARM
[63]
Governor Oil Standby Pump RUN ALARM
[64]
Turb.Guide Bearing Temp.HIGH ALARM
[65]
Turb. Guide Bearing Oil Temp. HIGH ALARM
[66]
Turbine GB.Oil Level LOW or HIGH ALARM
[67]
Turbine GB.CW.Flow LOW ALARM
[68]
Turb.GB.Oil Flow LOW ALARM
[69]
Shear Pin Broken ALARM
[70]
Gen.CB.Control Voltage Loss ALARM
[71]
Dynamic Brake or Gen.DS.FAULT ALARM
[72]
GCB.Ins.Gas Pressure LOW 1st ALARM
[73]
Uncomplete Start/Stop ALARM
[74]
Intake Gate Lower ALARM
[75]
Unit CO2 Under voltage ALARM
[76]
Control Deviation HIGH ALARM
[77]
Oil Pressure Tank Level LOW ALARM
[78]
Gov.Oil Res.Level HI/LO ALARM
[79]
Excit.AVR.Mode MANUAL ON
[80]
Unit Creep Detector Operated ALARM
[81]
Unit Sequence Controller TROUBLE ALARM
[82]
Turb.Shaft Seal CW.Pressure LOW ALARM
[83]
CO2 Locked ALARM
[84]
KG1A/C Sudden Pressure Relay ALARM
[85]
GROUP LAMP
[86]
KG1A / C Winding Temp. ALARM
[87]
KG1A/C Oil Temp Critical HIGH ALARM
[88]
KG1A/C Oil Temp.HIGH/FFS.Heat Detect. ALARM
[89]
KG1A/C Buchholz Relay ALARM
[90]
KG1A/C Oil Level LOW/Rubber Bag ALARM
[91]
KG1A/C DC/AC Supply Fail ALARM
[92]
-
[93]
TURBINE MANUAL
[94]
Line Charging TEST
[95]
-
[96]
PILOT LAMP